D-Nice said:I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?
D-Nice said:I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?
As above, yes. The two 120v lines an the neutral, without the high leg, are exactly, and I mean exactly, the same thing as a 120/240v 1-phase service.D-Nice said:I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?