Sub panel

Status
Not open for further replies.

D-Nice

Member
I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?
 
D-Nice said:
I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?

Yes .
 
D-Nice said:
I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?

Just keep in mind that you can't load up the transformer to its full kva on just 2 legs. . The rated kva is the result of multiplying I x E x 1.732. . It's that 1.732 that will get you in trouble if you try to load that full kva on just 2 legs.
 
D-Nice said:
I am a residential man so I don't work with 3-phase and haven't in 4 years. It's a 120/240 high leg system and I need to install a sub panel. Can I come off of the two "normal legs" and install a 1-phase 3-wire sub?
As above, yes. The two 120v lines an the neutral, without the high leg, are exactly, and I mean exactly, the same thing as a 120/240v 1-phase service.

In fact, the high leg service started out as a 3-phase conversion to an existing single-phase system. The open Delta merely adds a single transformer to one.
 
If it is an open delta, 1? load goes on to the transformer with the center tap ground at 100% and no load goes on the high leg transformer.

If it is a closed delta, two thirds of the load goes on that transformer while one third goes on each or the transformers that go to the high phase (yes, I know that that adds up to four thirds). :smile:
 