I would especially note you need an insulated EGC or "ground" wire.
If there is a pool house I bet it is a permanently installed pool.But isn't that only for a permanently install pool?
Not necessarily - read my post aboveAs well as the above advise, Please ensure there is a 4 wire feeder to the subpanel before using the subpanel to feed your feeder
Not necessarily - read my post above
.The subpanel that exists is for a pool so I am assuming it has an insulated egc. If it does not then the added panel would be in violation unless the original panel falls under 680.25(A) except. & (B)
can u run that feeder within 5 feet of the pool
680.25(A) exception will allow an existing panel to be used for pool equip. under certain situations..
I don't understand the exceptions. What do they mean?
680.25(A) exception will allow an existing panel to be used for pool equip. under certain situations.
680.25(B)(2) states that if there is an existing panel that is in a separate building that was fed with a 3 wire feeder (no egc), as previously allowed before 2008, then you can use that panel for pool equipment.