I have a customer who was a 200amp service on his house and he wants a 200amp service in hsi garage/welding shop. Can you install (2) 200 amp panels off one 200 amp service?
If the owner needs 200 amps of service at the garage then you will not have 200 amps to give him.
Just knowing it is a house implies the minimum required calculated loads, regardless of actual usage. That would preclude 200A being available for the garage from a 200A service for both.
Why? What do we know about the usage patterns at the house?
Why? What do we know about the usage patterns at the house?
No. My point is the actual usage is not the calculated load.Just knowing it is a house implies the minimum required calculated loads, regardless of actual usage. That would preclude 200A being available for the garage from a 200A service for both.
No. My point is the actual usage is not the calculated load.
If the house load is not running, just how does the calculated load at the house limit the actual current drawn at the garage?
Because we do not base service equipment ratings on actual usage unless it is greater than the minimum required calculated loads. Sure there may be 200A available for the garage with all house loads deenergized, but that would be an undersized, non-compliant service per the NEC.No. My point is the actual usage is not the calculated load.
If the house load is not running, just how does the calculated load at the house limit the actual current drawn at the garage?
Look again at the OP. It's the customer that wants the 200 A panel in the garage. I doubt that there is much more than a "this feels good" involved in the request by the customer.If the calculated load at the garage is 200 amps then you could not legally give the garage 200 amps when there is only 200 amps at the house whether the house is not being used or not. You cannot decide when and how each space is used.
I totally agree. This type of request is almost always a vanity intallation.I doubt he really needs 200 amps in the shop.
Look again at the OP. It's the customer that wants the 200 A panel in the garage. I doubt that there is much more than a "this feels good" involved in the request by the customer.
Laketime, what are some of the characteristics of this home / garage? Gas range, gas water heater, gas dryer ?
No but you can use a feed thru panel with 200 amp conductors.The answer is NO. You have to apply the NEC service calculations. Also you can not install a 200A OCPD in a 200A rated panelboard.