firelitr said:I'm a second stage apprentice electrician needing an answer to a question that no one seems to have: Why must the the neutrals be landed independant of the ground on a sub panel? I know the code says this shall be done, but why?
al hildenbrand said:Welcome th the Forum, Firelitr!
The image I like to use is about how we work hard to keep all the current (I'm not thinking of voltage - just current) in the hot wire, inside the hot wire until it reaches the load (light, motor, heater, etc.).
The return current needs to be given the same careful attention so it is kept inside a single insulated path. . .
That is, until it reaches the Service Disconnect. At the Service Disconnect, there will be the Main Bonding Jumper that connects the neutral and the equipment ground together, and from there on out to the Power Company transformer, the neutral is not separate. (In fact, in my opinion, the Power Company side of the Main Bonding Jumper is just plain messy. . .but that's not the point of your question).
Good wiring practice will result in the hot conductor current being physically close (same cable or raceway) to the neutral conductor current. The two currents are equal, but traveling in opposite directions. The magnetic field that each current creates is the opposite of the other, but of equal strength, so, they literally cancel each other out. . . .but only if all the current that comes out on the hot is returned only on the neutral.
In a sense, neutrals are constructed like spokes of a wheel. . .a single line from a hub (service disco) to the rim (the connected loads). The equipment grounding is not done this way. The equipment grounding is all interconnected where ever two or more different ones are in a junction box together. . .so the equipment grounds look, not like a spoke, but like a spiders web.
Any current that gets onto the spiders web like equipment ground will spread out and take all available paths back to the Power Company transformer (source), leaving an unbalanced magnetic field around the hot conductor.
That magnetic field can heat ferrous metals by inducing eddy currents into the them.
al hildenbrand said:Welcome th the Forum, Firelitr!
The image I like to use is about how we work hard to keep all the current (I'm not thinking of voltage - just current) in the hot wire, inside the hot wire until it reaches the load (light, motor, heater, etc.).
The return current needs to be given the same careful attention so it is kept inside a single insulated path. . .
That is, until it reaches the Service Disconnect. At the Service Disconnect, there will be the Main Bonding Jumper that connects the neutral and the equipment ground together, and from there on out to the Power Company transformer, the neutral is not separate. (In fact, in my opinion, the Power Company side of the Main Bonding Jumper is just plain messy. . .but that's not the point of your question).
Good wiring practice will result in the hot conductor current being physically close (same cable or raceway) to the neutral conductor current. The two currents are equal, but traveling in opposite directions. The magnetic field that each current creates is the opposite of the other, but of equal strength, so, they literally cancel each other out. . . .but only if all the current that comes out on the hot is returned only on the neutral.
In a sense, neutrals are constructed like spokes of a wheel. . .a single line from a hub (service disco) to the rim (the connected loads). The equipment grounding is not done this way. The equipment grounding is all interconnected where ever two or more different ones are in a junction box together. . .so the equipment grounds look, not like a spoke, but like a spiders web.
Any current that gets onto the spiders web like equipment ground will spread out and take all available paths back to the Power Company transformer (source), leaving an unbalanced magnetic field around the hot conductor.
That magnetic field can heat ferrous metals by inducing eddy currents into the them.
On the PoCo side, any current takes all available paths.al hildenbrand said:the Power Company side of the Main Bonding Jumper is just plain messy. . .but that's not the point of your question.
firelitr said:I'm a second stage apprentice electrician needing an answer to a question that no one seems to have: Why must the the neutrals be landed independant of the ground on a sub panel? I know the code says this shall be done, but why?
tom baker said:It is the most important part of the the premise wiring system
firelitr said:I'm a second stage apprentice electrician needing an answer to a question that no one seems to have: Why must the the neutrals be landed independant of the ground on a sub panel? I know the code says this shall be done, but why?