T thebugbear Member Aug 18, 2005 #1 What are the requirements for installing a main (cutout) breaker on a sub panel. I thought it was a matter of distance from the main panel and accessability. I am told that more than 6 breakers installed is also a criteria?
What are the requirements for installing a main (cutout) breaker on a sub panel. I thought it was a matter of distance from the main panel and accessability. I am told that more than 6 breakers installed is also a criteria?
petersonra Senior Member Location Northern illinois Occupation Semi-retired engineer Aug 18, 2005 #2 Re: Sub Pannel with 7 circuits you have to have a main disconnect if you have more than 6 breakers BUT it does not have to be part of the panelboard.
Re: Sub Pannel with 7 circuits you have to have a main disconnect if you have more than 6 breakers BUT it does not have to be part of the panelboard.
charlie b Moderator Staff member Location Lockport, IL Occupation Semi-Retired Electrical Engineer Aug 18, 2005 #3 Re: Sub Pannel with 7 circuits Duplicate. Closed. Please continue the discussion here.