Open Neutral
Senior Member
- Location
- Inside the Beltway
- Occupation
- Engineer
320A service feeding an adjacent outdoor 3R fused disconnect/EPO.
It in turn shall feed two PB's within the building, in different locations.
If each PB has a main breaker of ~100A, does the cable from the disconnect to each PB need to be sized for 320A or ~100A?
I'd think 320 but something is tickling my memory about this.
The EC wants to instead install 2 disconnects/EPO at the meter, each fused at 100A. If so, do the PB's still need their own main breakers?
(My alternative is one disconnect followed by a 3R PB with 100A breakers feeding each PB, again [not] needing 100 PB mains.)