lexkyphil
Member
- Location
- Lexington, Kentucky
I have a natural gas compressor building that has a 5' deep subfloor area with open grating as the deck above. The building is power ventilated to 6 air changes per hour to keep it class I, div II. There is air being introduced below the floor at a high rate. We are using separate cable trays with 13.2kV MV105cable, various 120-480 power cables and control cables, all type TC, per 501.10 (B)(6). Is this area still to be classified as Division I? If so, I have to use ITC-HL or MC-HL. Would like to avoid using a different cable type. What are your thoughts?