T timm333 Senior Member Location Minneapolis, MN Occupation Electrical Design Engineer Oct 6, 2020 #1 Can THW cable be used for the power of submersible pump motor? NEC 680.51(E) does not give much information. Thanks
Can THW cable be used for the power of submersible pump motor? NEC 680.51(E) does not give much information. Thanks
ptonsparky Tom Location NE (9.06 miles @5.9 Degrees from Winged Horses) Occupation EC - retired Oct 6, 2020 #2 Not down the hole, but out to it. Use pump cable.
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 6, 2020 #3 UL lists a submersible pump cable, thats what most pump installers use. Art 680 is swimming pools a more appropiate article would be 310-Conductors
UL lists a submersible pump cable, thats what most pump installers use. Art 680 is swimming pools a more appropiate article would be 310-Conductors
T timm333 Senior Member Location Minneapolis, MN Occupation Electrical Design Engineer Oct 13, 2020 #4 We have a junction box in between MCC and submersible pumps. Just to confirm, THW can be used from MCC to junction box, and then UL rated submersible pump cable from junction box to submersible pump. Is it correct?
We have a junction box in between MCC and submersible pumps. Just to confirm, THW can be used from MCC to junction box, and then UL rated submersible pump cable from junction box to submersible pump. Is it correct?
tom baker First Chief Moderator & NEC Expert Staff member Location Bremerton, Washington Occupation Master Electrician Oct 13, 2020 #5 Yes