In a landfill gas condensate pump application (knockout pot in the gas flowstream), I've come across a couple vendors nearly identical statements providing what I assume is 'self-evaluation' of their equipment for hazardous location installation.
https://www.epgco.com/wp-content/uploads/2016/10/0385c-Class1Div1.pdf
Assuming the installed location is Class I, Division 1 (although this is under some internal debate), do you think the design described in the document meets the intent of 501.125(A)(4), and/or the self evaluation requirements of 500.8((A)(3). Am I correct in stating that if this evaluation is sufficient, the equipment would still need to be marked as required in 500.8(C)?
If the area is Class I, Division 2, then I believe the design/documentation is probably sufficient for 501.125(B). But for Div 1, I think they need to label the equipment - is this correct?
Using the 2017 NEC.
https://www.epgco.com/wp-content/uploads/2016/10/0385c-Class1Div1.pdf
Assuming the installed location is Class I, Division 1 (although this is under some internal debate), do you think the design described in the document meets the intent of 501.125(A)(4), and/or the self evaluation requirements of 500.8((A)(3). Am I correct in stating that if this evaluation is sufficient, the equipment would still need to be marked as required in 500.8(C)?