An AHJ which will remain nameless has started requiring what they call a "fault current calculation" for all commercial PV projects, by which they mean a summing of the AFC from the utility at the terminals of the utility transformer and the AFC from the inverter(s) at its/their terminal(s).
 
I've noticed a large upturn in clients needing arc fault studies in the last year. They will get all the way through installation and then come back with a change order asking for an AF study because the AHJ requires detailed labels.
 
Sounds like someone is making you guys some more work
That's what I thought at first; a real available fault current calculation is not necessarily straightforward, so I started asking questions about what point in the system they wanted the calculation done for and what the conductors were, etc., but then my client showed me one that passed. AFC at the transformer plus AFC at the inverter(s). OK, that's easy, but I don't see the significance of the result.
 
That's what I thought at first; a real available fault current calculation is not necessarily straightforward, so I started asking questions about what point in the system they wanted the calculation done for and what the conductors were, etc., but then my client showed me one that passed. AFC at the transformer plus AFC at the inverter(s). OK, that's easy, but I don't see the significance of the result.
CYA?

I now how to spell souler, and that's about it
 
An AHJ which will remain nameless has started requiring what they call a "fault current calculation" for all commercial PV projects, by which they mean a summing of the AFC from the utility at the terminals of the utility transformer and the AFC from the inverter(s) at its/their terminal(s).
Why should they remain nameless? If you recall a week or so ago I had a thread on a inspection failed by Seattle sdci. Obviously I named the ahj, I did not name the inspectors involved, but I would have if my appeal had been unsuccessful. Why hide the information?
 
An AHJ which will remain nameless has started requiring what they call a "fault current calculation" for all commercial PV projects, by which they mean a summing of the AFC from the utility at the terminals of the utility transformer and the AFC from the inverter(s) at its/their terminal(s).
Since inverters shut off under fault conditions when the voltage is out of spec, is this really any different than the fault current calculation for a service and distribution system in general? Even if you account for the maximum possible current, it's still small enough that it is barely even a rounding error, in most cases.

It is common that utilities have a field on their interconnection applications for inverter fault contribution current, and until manufacturers started adding it to the datasheet, I had no idea where to even begin. Usually, this ends up either matching the continuous output current, or just being slightly more than it, but not really enough to swing a design decision. The applications are likely written with rotating generators in mind, where this is significantly larger than the full load amps.
 
Can the AFC of an inverter be higher than the ISC of the modules due to energy stored in the capacitors and inductors of the power electronics? (I would guess yes, but not a lot)
All capacitors are ignored when performing fault current calculations.
 
I see on this forum that most hide their information, maybe they are afraid of some type of retribution ?
 
I know that caps store very little energy, but it can be discharged very quickly. Ever run any numbers on what the contribution of a large PFC bank would be?
I dont think any software, like Etap or SKM, considers any capacitor contribution at all, even if I wanted it to. Motors have a decaying magnetic field which can contribute some fault current.
 
Yeah but are AHJs necessarily logical?
In a meeting a couple of years ago, a rep of an AHJ took the opportunity to bring up a disagreement we had over another completely unrelated issue that had occurred a couple of years before. Before I could stop myself I told him he had been wrong then and was still wrong. The meeting did not go well after that.
 
In a meeting a couple of years ago, a rep of an AHJ took the opportunity to bring up a disagreement we had over another completely unrelated issue that had occurred a couple of years before. Before I could stop myself I told him he had been wrong then and was still wrong. The meeting did not go well after that.
How does "shoe" taste??
 
Since inverters shut off under fault conditions when the voltage is out of spec, is this really any different than the fault current calculation for a service and distribution system in general? Even if you account for the maximum possible current, it's still small enough that it is barely even a rounding error, in most cases.

It is common that utilities have a field on their interconnection applications for inverter fault contribution current, and until manufacturers started adding it to the datasheet, I had no idea where to even begin.
While inverters would shut down this functionality is not considered a protection function under the arc fault calculations. So the calculations are done assuming that an inverter is able to output its fault current indefinitely into a fault and it would only be interrupted by a fuse or CB in the circuit path.

While inverter manufacturers have been a little better about publishing the fault current they almost all fall into the range of 1.2-1.3X the FLA. I've always defaulted to 1.2X myself if no other information is available.

Can the AFC of an inverter be higher than the ISC of the modules due to energy stored in the capacitors and inductors of the power electronics? (I would guess yes, but not a lot)
In the arc fault calcs, the output of the inverter is modeled based on a multiple of the rated output and that's it. The internal capacitors and inductors are not evaluated as adders. But their existence is part of the reason the fault current from an inverter is 1.2-1.3X the rated output.

All capacitors are ignored when performing fault current calculations.
The 2021 NFPA 70E has a new annex R that covers capacitors and electrical safety issues. It covers the arc flash hazards of capacitor banks and SKM can use capacitor banks as a source in the arc flash calcs. It's a newer area though so the application is still inconsistent.
 