subpanel bonding

Status
Not open for further replies.
Re: subpanel bonding

sorrry Yes the bonding screw it is 240 volt 4 conductor from the main that is bonded with the screw the sub has 2 GFCI breakers for the tub it is fed in PVC conduit to the subpanel
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Re: subpanel bonding

Originally posted by redanntony:
sorrry Yes the bonding screw it is 240 volt 4 conductor from the main that is bonded with the screw the sub has 2 GFCI breakers for the tub it is fed in PVC conduit to the subpanel
Throw away the bonding screw. Your grounded and grounding conductors should be separate at the subpanel. The grounded conductors will terminate on the neutral bar and grounding conductors will terminate on a equipment grounding bar.
 