Subpanel breaker size, two refrigeration condensing units

Merry Christmas
Status
Not open for further replies.

samsmart

New User
Location
Bakersfield, CA
Occupation
Property Maintenance Tech.
My questions is amp sizing for a subpanel. I am looking to install a subpanel (30ft away from main) that would be used to connect two identical 2-ton condensing units 230V for two 5-door drinks coolers next to each other in a market. The label for each condensing unit indicates the following: RLA = 15.7, LRA = 68.0, MINIMUM CIRCUIT AMP = 21.0. AMPS.MAX.BRANCH CIRCUIT FUSE = 40.

What size double pole breaker (and wire size) do I use for the subpanel? Do I add both max circuit fuse (80A)?
 