Subpanel capacity

Status
Not open for further replies.

Open Neutral

Senior Member
Location
Inside the Beltway
Occupation
Engineer
WA State
PSE
Building with two 200A disconnects with appropriate gauge to front & rear PB's.

One feeds an existing 100A PB with a 100A Main {It was the building's main before upgrades....}
And 20A breaker to solar supply. Others to misc. loads.

The client was told that any further array expansion would require replacing the PB with a 200A one.
Thinking about, I wonder why.
If you can consume 80% of 100A, can't you source that into the panel?
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
It is often correct that a 100A panelboard with a 100A main breaker can not be backfed by more than a 20A breaker. This is the traditional "120% rule" that limits how much interactive inverter output can be interconnected to a panelboard. It is no longer the only rule, but seems to be the one that is being cited.

(Strictly speaking the backfeed limit is not about the solar breaker but is 125% of nameplate inverter output. So the limit on the panel you describe would be 16A inverter output, which requires a 20A breaker.)

Replacing the panelboard with a 200A is not the only possible option. Other options could be:
- See if the sum of breakers in the panelboard is 100A or less.
- Replace with a 125A panel (would allow backfeeding 40A on a 50A breaker).
- Downsize the breaker feeding the panel if the calculated load does not require it to be 100A. (Not possible for a 100A service disconnect due to other rules, but I believe you're describing a downstream feeder breaker).

As for why, don't overthink it, just read 705.12. Exact numbering has changed in each cycle so tell us your code cycle for a more specific reference.
 