I help some home inspectors in my area with questions they have. An inspectors asks:
"Here is my dilemma. My clients have their main electrical panel in the garage. It is a 200 amp panel, with shut off , likely only 5 to 8 years old. Since the panel is over 15 ft. from the meter (outside, with shut off) the clients have been told that the panel in the garage is a sub- panel and grounds/neutrals should be separated."
I replied -"2 thoughts.If there is an outdoor disconnect after the meter, any panel after that is considered a subpanel. Period. This would have also required that the cable AFTER the outdoor disconnect that runs to the panel be SER cable. Round not flat. 4 conductors. 2- hots, 1 neutral and 1 ground.
Regarding subpanels and unfused conductors. After the meter, the submain cable can run almost anywhere outside but when it enters the building it must be protected (breaker/fuse) within 3-5 feet, not sure).
I suspect the panel is on an interior wall, hence the outdoor disconnect."
He replied - "Thanks again for your fast response and knowledge. One question ?.do the neutrals and grounds have to be separated in the sub-panel, that is located on the interior wall. (Rear wall of garage) I do believe that the cable running to the panel is SER, but from memory I can not be 100% sure. One other question?..sorry ??what if the sub main cable is flat (3 conductor) ????"
He's not listening.
Please, a good, easy explanation of subpanel connections.....
"Here is my dilemma. My clients have their main electrical panel in the garage. It is a 200 amp panel, with shut off , likely only 5 to 8 years old. Since the panel is over 15 ft. from the meter (outside, with shut off) the clients have been told that the panel in the garage is a sub- panel and grounds/neutrals should be separated."
I replied -"2 thoughts.If there is an outdoor disconnect after the meter, any panel after that is considered a subpanel. Period. This would have also required that the cable AFTER the outdoor disconnect that runs to the panel be SER cable. Round not flat. 4 conductors. 2- hots, 1 neutral and 1 ground.
Regarding subpanels and unfused conductors. After the meter, the submain cable can run almost anywhere outside but when it enters the building it must be protected (breaker/fuse) within 3-5 feet, not sure).
I suspect the panel is on an interior wall, hence the outdoor disconnect."
He replied - "Thanks again for your fast response and knowledge. One question ?.do the neutrals and grounds have to be separated in the sub-panel, that is located on the interior wall. (Rear wall of garage) I do believe that the cable running to the panel is SER, but from memory I can not be 100% sure. One other question?..sorry ??what if the sub main cable is flat (3 conductor) ????"
He's not listening.
Please, a good, easy explanation of subpanel connections.....