I have a friend who built a 25x30 metal building. He is wanting electric ran to his building from his main panel located approx. 160 feet away in his main residence. He is pretty much just wanting some lights and recepts. along with a receptacle for a window a/c unit. I believe the load on the a/c unit will be around 15 amps max probably less and his lighting and receptacle load will be minimum. I am going to size his feeder for 60amps max. continuous. I have performed some voltage drop calculations and due to the distance, I have come up with #2 awg feeder size at a maximum continuous load of 60 amps with no more than 3% voltage drop on the 120V side. I am looking for some confirmation from anyone else who may read this. Please advise. Thanks!