Re: Subpanel Grounding
jeff43222 said:
Suppose he did the installation as described above. From a physics standpoint, why is it bad?
It's not bad, because its not dangerous. However, that relies on there really being no metal paths between the house and the barn, and no such paths ever being constructed in the future.
The physics of what happens in the barn is the same as in the house. You bond the N-G at the main panel, and at no other panel downstream. From any load anywhere in the house, the neutral current will travel along the neutral wire to the source. No current will travel along the EGC (or along any conduit, etc.) unless and until there is a fault within some piece of equipment. When the fault happens, the fault current travels along the EGC to the N-G bond, and from there to the source. This quickly trips the breaker. If you happened to be touching the tool when it has its failure, you may receive a shock, but it will be brief.
If the barn has no EGC in its feeder, and if the N-G is bonded at the barn's first panel (and at no other panel in the barn), then any neutral current from any load in the barn will travel along the neutral of the branch circuit to the barn panel, and along the neutral of the feeder to the source. That does not create a hazard to anyone operating a tool inside the barn. However, if a tool does experience a failure, then the fault current will travel along the EGC within the barn to the N-G bond at the barn panel, and from there along the neutral of the barn's feeder to the neutral of the main house panel. This will trip the breaker, and the person holding the tool may or may not feel a short shock.
The danger would come about if there were metal pipes between the buildings (or if metal pipes get installed at a future date). In that case, even under normal operation with no faulted equipment, neutral current from a tool inside the barn would travel along the neutral wire of the branch circuit to the barn's N-G bond, and from there along BOTH the neutral of the barn's feeder AND the metal pipe back to the house. This would energize the metal pipes (and other external metal parts of electrical equipment) within the house.