and by creating the second (parallel) path for the neutral, the egc becomes essentially another neutral, so that any current that is supposed to be travelling on the neutral is now shared on the egc, energizing any conduits, boxes, ceiling grids, metal studs, or metal parts on the way back to the source. the situation becomes worse if the neutral gets damaged, loose or broken, then all the neutral current is now on the egc, and because all the equipment is still functioning properly no one finds out until someone is killed or injured, perhaps an electrician taking apart a piece of coduit or box who unknowlingly becomes part of the circuit. the egc is designed to carry fault current only in order to trip ocpd's, not to be a grounded conductor.