Re: Subpanel grounding
In order to guard against the possibility of a high impedance condition on the neutral conductor between two panels located in the same building the separate Equipment Grounding Conductor (EGC) is required. With a separate EGC and the neutral of the feeder kept aloof from ground at all points beyond the service disconnect you can avoid having neutral currents flowing on interior metal piping and other metallic systems and structural components that are not designed to carry current. The code permits the use of the second ground rod at the feeder supplied panel but it may only be connected to the EGC at that point and not to the grounded conductor.
250.54 Supplementary Grounding Electrodes.
Supplementary grounding electrodes shall be permitted to be connected to the equipment grounding conductors specified in 250.118 and shall not be required to comply with the electrode bonding requirements of 250.50 or 250.53(C) or the resistance requirements of 250.56, but the earth shall not be used as the sole equipment grounding conductor.
#1 does code require a ground wire bonding between rods and panels.
The Code requires an EGC between the two panels that is run with the feeder conductors in the same raceway or cable.
#2 If so is the separation of the grounding bus & the neutral bus required in the sub panel.
Yes, you must keep them separate.
250.24 Grounding Service-Supplied Alternating-Current Systems.
(A) System Grounding Connections. A premises wiring system supplied by a grounded ac service shall have a grounding electrode conductor connected to the grounded service conductor, at each service, in accordance with 250.24(A)(1) through (A)(5).
(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
#3 Can the sub panel be treated the same as a sub panel noted in 250.32/A of the NEC which allows either a grounding rod or a pulled bonding wire.
The answer to this question is contained in the title of the article you are asking about. It reads "250.32 Two or More Buildings or Structures Supplied from a Common Service." You are not talking about two buildings but rather two sections of the same building. Even if it were two buildings it would need to be free of any other metallic pathways between the two structures in order to be acceptable without an EGC that is run with the feeder in the same raceway cable or trench.
It is also worth noting that, in the case of
separate buildings, if there is more than a single branch circuit to the second building it is required to have a grounding electrode system regardless of whether or not an EGC was run with the feeder. So it is not a choice between a "either a grounding rod or a pulled bonding wire" but rather a choice between whether or not to run an EGC to a separate building that is free of any metallic pathways between it and the building in which the feeder supplying it originates.
--
Tom