I've gotten a few bids from some electrical contractors to install a subpanel for my garage. I have 200 amp service at my house, and different contractors have quoted different sizing for the subpanel.
I realize the actual capacity of my panel will vary based upon the actual load of the equipment using it. I don't have all of that information, and may not have it all until after the electrical is complete. So, I thought it would be a good idea to calculate the theoretical headroom assuming the devices use the maximum VA supported by the proposed circuits.
Here are the circuits going into the subpanel:
Air compressor (240v * 25 amp = 6000 VA)
Ductless mini split (240v * 30 amp = 7200 VA)
2-post car lift (240v * 30 amp = 7200 VA)
Tesla charger (240v * 60 amp = 14400 VA)
Misc outlets (500 sqft * 3VA = 1500 VA)
Total VA = 36,300 VA
Adjustment per NEC 220.82
------------------------------------
100% of the first 10kW = 10,000 VA
40% of the remainder = (36,300-10,000) *4 = 10,520VA
Total Adjusted VA = 20,520 VA
Total Adjusted Amps = 20,520/240 = 85.5 amps
If all of that is correct, then I basically need to choose between 100 amp or 125 amp subpanels. Of the 3 quotes I got, only one quoted a 100 amp panel. They also happen to be _half_ the cost of the other two bids. If the above calcs are correct, I'll have at least 8700 VA left of headroom. I believe that means I have room for another 240v 30 amp circuit or a couple of 120v circuits. Are my calculations above correct?
Thanks!
I realize the actual capacity of my panel will vary based upon the actual load of the equipment using it. I don't have all of that information, and may not have it all until after the electrical is complete. So, I thought it would be a good idea to calculate the theoretical headroom assuming the devices use the maximum VA supported by the proposed circuits.
Here are the circuits going into the subpanel:
Air compressor (240v * 25 amp = 6000 VA)
Ductless mini split (240v * 30 amp = 7200 VA)
2-post car lift (240v * 30 amp = 7200 VA)
Tesla charger (240v * 60 amp = 14400 VA)
Misc outlets (500 sqft * 3VA = 1500 VA)
Total VA = 36,300 VA
Adjustment per NEC 220.82
------------------------------------
100% of the first 10kW = 10,000 VA
40% of the remainder = (36,300-10,000) *4 = 10,520VA
Total Adjusted VA = 20,520 VA
Total Adjusted Amps = 20,520/240 = 85.5 amps
If all of that is correct, then I basically need to choose between 100 amp or 125 amp subpanels. Of the 3 quotes I got, only one quoted a 100 amp panel. They also happen to be _half_ the cost of the other two bids. If the above calcs are correct, I'll have at least 8700 VA left of headroom. I believe that means I have room for another 240v 30 amp circuit or a couple of 120v circuits. Are my calculations above correct?
Thanks!