M mtn_elec Senior Member Dec 1, 2005 #1 Does anyone know what the height requirement for the highest circuit breaker handle in an apartment for disable people is?
Does anyone know what the height requirement for the highest circuit breaker handle in an apartment for disable people is?
J jbwhite Senior Member Dec 1, 2005 #2 Re: subpanel height sounds like a labor and industry question.
hey_poolboy Senior Member Location Illinois Dec 2, 2005 #3 Re: subpanel height Sounds like an ADA question to me, but I still don't know the answer mike
roger Moderator Staff member Location Fl Occupation Retired Electrician Dec 2, 2005 #4 Re: subpanel height To go with other ADA reach limits it would be 54" if it can be accessed from the side of a wheel chair, or 48" if only front access is possible. Roger
Re: subpanel height To go with other ADA reach limits it would be 54" if it can be accessed from the side of a wheel chair, or 48" if only front access is possible. Roger
ryan_618 Senior Member Location Salt Lake City, Utah Dec 2, 2005 #5 Re: subpanel height It depends on what code New Jersey adopts for accessiblity. If it is the ADAAG, go with what Roger says. If it is the ICC/ANSI A117.1, 48" is the max, with no provisions for a 54" unobstructed side approach.
Re: subpanel height It depends on what code New Jersey adopts for accessiblity. If it is the ADAAG, go with what Roger says. If it is the ICC/ANSI A117.1, 48" is the max, with no provisions for a 54" unobstructed side approach.
M mtn_elec Senior Member Dec 2, 2005 #6 Re: subpanel height Thank You guys for your info, very helpfull.