I inspected a single family dwelling today and I looked into a closet and saw subpanel inside the closet. Is this a violation?
That would depend first if this is a clothes closet. Article 240.24(2)(D) 2008 edition say shall not be located in the vicinity of easily ignitable material, such as clothes closet. Next would be to make sure that proper working clearance have been provided.
Agreed. What inspectors have told me is "if it has a rod, for hanging clothes, mounted in it then it is a clothes closet and it would be a no no".That would depend first if this is a clothes closet. Article 240.24(2)(D) 2008 edition say shall not be located in the vicinity of easily ignitable material, such as clothes closet. Next would be to make sure that proper working clearance have been provided.
And if it dosen't have a rod, it will as soon as you leave :slaphead:Agreed. What inspectors have told me is "if it has a rod, for hanging clothes, mounted in it then it is a clothes closet and it would be a no no".
Just so long as it is not a water closet...It's not a "clothes closet," it's an "electrical closet." :happyyes: I put them in buildings all the time. :happyyes: OK, I will admit that I don't usually include a horizontal wooden rod in the design. :happyno:
It is interesting to hear some of the cmp members talk on this. In their opinion if the panel were behind the swing of a door and not near the clothing then it would not be an issue. Think of a wall perpendicular to the the door entry where the doorswings onto the perpendicular wall. In that case it should be fine but I don't know many ahj's who will buy that.
And a horizontal rod would not work for that purpose. You would need either a shelf or a hook.... I would want something to hang my hat on.
Are their approved drawings for this site? If you have stamped drawings what do they call out? If the stamped drawings define this as a clothes closet, then it does not matter if there is a rod present or not. Either way before I called this out as a violation I would want something to hang my hat on.
Simply because it is not next to clothing or combustibles. Let's face it how often have you seen a panel arc thru the cover.What's thier reasoning for thinking this would be ok?
Simply because it is not next to clothing or combustibles. Let's face it how often have you seen a panel arc thru the cover.
I am thinking that clothing can be extremely flammable and if you remove the cover and work on a hot panel then it is possible to have an arc and the clothing could ignite. If the panel is behind a door it would appear safe.
I inspected a single family dwelling today and I looked into a closet and saw subpanel inside the closet. Is this a violation?
Not that ignorance is something that the code can address, but I often find during re-meter inspectins the covers missing and the tenant or owner having to search long and hard before finding them, sometimes they can?t produce them