subpanel neutral and ground

Status
Not open for further replies.

lutron

Member
Location
Pennsylvania
we all know that in a subpanel in the same structure we dont connect grounds and neutrals but could somebody give me a 2002 nec reference thanks.

mike
 

BAHTAH

Senior Member
Location
United States
Re: subpanel neutral and ground

250-24(5). Locations where a grounding connection would be allowed after the main would be locations such as separately derived system or separate buildings meeting specific conditions. 250-30(A) and 250-32.

[ July 18, 2003, 06:08 PM: Message edited by: grant ]
 