CAN I USE #2 ALUMINUM FOR A 100AMP SUB=PANEL IN A RESIDENTIAL HOME??? CAN I USE CHART 310.15(B)(7)?? IS THIS CONSIDERED A FEEDER>??
Welcome to the forum :thumbsup:CAN I USE #2 ALUMINUM FOR A 100AMP SUB=PANEL IN A RESIDENTIAL HOME??? CAN I USE CHART 310.15(B)(7)?? IS THIS CONSIDERED A FEEDER>??
thanks for your reply. Where can I find that in the code? The sub-panel is actually 100% of the load. I added a new 200amp panel and out of that panel I added a 100amp sub-panel. This is taking the place of the old 100amp main panel. The 200amp panel currently does not have any other circuits. I ran #2SER to the 100 amp panel and the inspector said it has to be a 90amp.
According to 310.15(B)(7) it says: " For application of the section, the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling.
To me this means if I add a sub panel it is considered a feeder and I should be able to run #2SE cable with a 100 amp main. One township said it is considered a feeder and ok for me to use this chart to size my wire and another township said its not a feeder!!
Whats everyones input?? I was told by one inspector that this has been a change over the years and that I am good to go with the #2 aluminum for a 100 amp sub-panel since it is a feeder.
The 200amp panel has no other circuits in it currently. It has a 100 amp 2pole feeding a sub-panel. The sub-panel use to be the main panel at one point when it was only a 100amp service. The sub-panel is currently carrying the total load of the house.
IMO, no but yes it should be considered. The T. does not state we have to take derating into consideration.If it's installed in thermal insulation would a 75 amp OCPD need to be used?
The inspector is looking into the future with his crystal ball. Like him we all know that someone will at some point add a circuit to the 200 amp panel.
From what I'm gathering, there is a 100A breaker supplying your feeder... and it is not the main disconnect.According to 310.15(B)(7) it says: " For application of the section, the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling.
To me this means if I add a sub panel it is considered a feeder and I should be able to run #2SE cable with a 100 amp main. One township said it is considered a feeder and ok for me to use this chart to size my wire and another township said its not a feeder!!
Whats everyones input?? I was told by one inspector that this has been a change over the years and that I am good to go with the #2 aluminum for a 100 amp sub-panel since it is a feeder.
According to 310.15(B)(7) it says: " For application of the section, the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling.
Sorry, but I believe you are reading it wrong...Smart,
Feeders between the main disconnect and the panelboard that supplies 100% of the house loads qualify. Any feeders in between that serve 100% of the house load are going to be between the main disconnect and the last panel that does.
Sorry, but I believe you are reading it wrong...
...the main power feeder shall be the feeder between the main disconnect and the panelboard that supplies, either by branch circuits or by feeders, or both, all loads that are part or associated with the dwelling.
What needs to be clarified here is whether the the 200A panel is MLO, with an SEC feeding it and the 100A breaker is the only main disconnect (i.e. the only service disconnecting means) for the dwelling. If there is a service disconnect ahead of the 100A breaker, then IMO it does not qualify... even though it is carrying 100% of the dwelling load.
The susceptibility of adding dwelling loads to the 200A panel doesn't matter as far as code is concerned. But why install a 200A panel? Surely not to just put one two-pole breaker in it...:slaphead: