Theoretically, do you prefer a main lug or main circuit box. For example, a 100 amp box installed in a garage connected by #2 copper wire with a #6 ground run through inch and a quarter conduit.
Grey Eagle said:Theoretically, do you prefer a main lug or main circuit box. For example, a 100 amp box installed in a garage connected by #2 copper wire with a #6 ground run through inch and a quarter conduit.
Grey Eagle said:Theoretically, do you prefer a main lug or main circuit box. For example, a 100 amp box installed in a garage connected by #2 copper wire with a #6 ground run through inch and a quarter conduit.
georgestolz said:If you want the convenience of an extra handle to kill the panel you're about to work in, a MDP wouldn't be a bad idea. However, I think from a safety standpoint, the MDP is a bit misleading because the panel is still energized if you shut off that main breaker. So, PPE would still be required.
I use MLO's every day, and don't have a problem with it. There are specific times to use the different types, it just depends on the application.
georgestolz said:Larry, since the components you mentioned are energized, then PPE is technically required, right? It's convenient for me to just work an MLO panel hot, too, but that's not a great idea without PPE.
I'm saying, I think from a safety standpoint, you decrease the chances of getting nailed by shutting off the busses, but you're still working in a live panel, right?
You are not permitted to work in or on energized electrical equipment with or without PPE other than the very limited exceptions. The most notable of which is troubleshooting.Larry, since the components you mentioned are energized, then PPE is technically required, right? It's convenient for me to just work an MLO panel hot, too, but that's not a great idea without PPE.
If you are working on a panel that meets the Canadian Electrical code, I would agree, but not if working on a typical US panel. The Canadian Code requires an additional interal metal cover over the line terminations.Actually, I'll have to check this but, I think once you have turned off main breaker, and confirmed breaker opened all lines with power, you can then do the work without the PPE.
don_resqcapt19 said:Larry,
If you are working on a panel that meets the Canadian Electrical code, I would agree, but not if working on a typical US panel. The Canadian Code requires an additional interal metal cover over the line terminations.
Don
Unless you are self employeed the agency is OSHA.This application certainly sounds residential. If so, what regulatory authority requires PPE?