Starplex
New member
- Beaumont, TX
I have done extensive searches, but have yet to find an exact answer to my question. So I purchased a home this year that was built and wired (all copper) in 2000 and included a detached shop. It has a 200amp service to the main breaker. (Note:the house uses mostly natural gas, thus electric load is minimum). Out of the main breaker box they wired a subpanel into the garage (100 amp breaker). The subpanel was wired using 1/0 (3 wire w/o ground, obviously not in compliance with 2008 code, but okay for 2000?). Out of this subpanel they pulled feed to the detached shop, using two #2 AWG hot conductors (underground pvc) and one #4 AWG neutral conductor (no 4th wire ground). These conductors come up on the outside of the shop to a small breaker box (4 spaces) and have a single 100 amp breaker. It then leaves this box with two #2 AWG hot conductors and one #2 AWG neutral conductor to a 40 space panel inside the shop. In both the shop and garage panels the grounds and neutrals are co-mingled on the neutral bus, thus bonded.
I am installing a small central A/C unit in the detached shop and have the following questions: 1). should the neutrals & grounds be seperated in the panel in the detached shop? Since there is no 4th ground wire, should the grounding bus go to a grounding rod at the detached shop? Currently there is no grounding rod, but I can install one. If not bonded, and grounds seperated the grounds will just terminate at the box. Or do I leave as is.
2). For the subpanel in the garage, I cannot pull a 4th wire (two story house), thus should I leave this panel as bonded, as is or separate grounds and neutrals? Sorry for the long post.