Stevenfyeager
- United States, Indiana
- electrical contractor
We've agreed that a 100 subpanel in a house requires #1 AL and not #2 like all electricians around here have been running for decades. (Although there is only one inspector in this area that requires larger than #2, because he says a subpanel is not a service) (and the older NEC books which they still use has the dwelling services sizing table instead of 2017 book, 83 %). Does that include wire from an outside disconnect? Is that considered a service or a branch circuit?
Which makes me ask, when we run 4/0 AL from an outside disconnect to a 200 amp house panel, is that sufficient? Table 31.15b says 4/0 AL only carries 180 amps. Thank you.