billiards4me
Member
- Location
- United States
I'm working on a detached maintenance building at a subdivision. There is a pole mounted meter and panel. Out of that panel, previously was run 2 phases and 1 neutral, no ground. Direct burried approx 200' to the old maintenance building. The new building has been constructed an additional 80'+ further away. I tapped on to my 3-wire system and extended to my new panel in the building. I set a rod, and bonded the panel with the bonding screw (also bonded building steel, because it's a metal building.). Inspector came out and said that since this is a sub panel, it needs to be a 4-wire system from the original panel on the pole at the meter, and to take the bonding screw out of my new sub panel. I agree with most of this, although I thought I remembered something in the code where if the sub panel is not attached to the main building (in this case there is no main building, just a pole) and if it's more than 100' away, that you could run a 3-wire system to it, and re-establish a ground with your rod, and bond the panel. Can anyone please point me in the direction to find such code, or let me know if this is barking up the wrong tree? Thanks guys!