What violations are visible in pic?

HI said working space and height of breakers, was he correct?

Says files too large so not able to post pics yet, I'll post this anyway until someone tells me how to fix

(No problem posting the pics on ET)
 

letgomywago

Senior Member
Location
Washington state and Oregon coast
Occupation
residential electrician
If this is correct orientation then it doesn't meet the rule for up is on and down is off.

No coupling on the liquid tight sleeve

Working space but the rule for existing buildings allowing less height than normal I feel shouldn't be allowed at this point.
 

readydave8

re member
Location
Clarkesville, Georgia
Occupation
electrician
If this is correct orientation then it doesn't meet the rule for up is on and down is off.

No coupling on the liquid tight sleeve

Working space but the rule for existing buildings allowing less height than normal I feel shouldn't be allowed at this point.
I hadn't thought about orientation of breakers, thanks

The sealtight is sleeving romex, romex has connector where it enters box, I feel like that end is ok. Other end has Sealtight connector in handybox, so I'm not sure I'd consider romex secured

And thanks for picture magic! Maybe next you can help me with on-line Social Security form?😉
 

norcal

Senior Member
If this is correct orientation then it doesn't meet the rule for up is on and down is off.

No coupling on the liquid tight sleeve

Working space but the rule for existing buildings allowing less height than normal I feel shouldn't be allowed at this point.
What it was installed before that rule took effect? A lot of manufacturers made them that way in the past.
 

hillbilly1

Senior Member
Location
North Georgia mountains
Occupation
Owner/electrical contractor
When you select the picture, click on “Show picture” then click on “Actual size”, and it will give you a pop up list of file sizes you can use, then just click on the smaller file size. At least that’s how Apple works
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
Yes but white started late 70s. It was black, white, pink, and blue then but not standardized. Idk how to tell mc age without looking at it but I can tell old AC from newer mc and ac. When did old school AC stop being galvanized I guess.
While the manufacturers use standard colors, there is nothing in the product standard to require the use of those colors. If someone wanted to make 14AWG copper with a yellow or orange jacket, there is nothing to prevent that.
 