Hello everyone- I just recently got back into electrical work and eager to start learning. I was in a house a few days ago and noticed that they had a 6-3 wire going to the subpanel on a 60 amp breaker. My question is with the subpanel. It was a 100 amp main breaker with about 10 circuits in it. 4 were going to the kitchen, sump pump , outlets, and lights. Is it legal to do that. It just seemed to be a lot on 60 amps. Thank you and look forward to learning more.
 
The only way to ensure that the 60 amp feeder is adequate is to perform a load calculation. Just eyeballing circuit breaker sizes won't tell you much.

When you have a moment plus update your profile to include your occupation. Thanks.
 
Yes I definitely know what you mean as far as comparing to a main panel. I will try to do a load calculation. As far as the the 100 amp box I assume it’s ok to have only 60 amps going to it?
 