Subpanels

Status
Not open for further replies.

brocc71460

Member
Location
New Jersey
I recently installed a GE subpanel in a residence. I removed the jumper from one side of the neutral buss to the other. I bonded the one side with the bonding screw provided. I used this side for all my grounds and the other side for all my neutrals.The inspector failed me. His justification was that the panel was not designed for this purpose. Is he correct?
 

curt swartz

Electrical Contractor - San Jose, CA
Location
San Jose, CA
Occupation
Electrical Contractor
Re: Subpanels

If the instructions that came with the loadcenter didn't specifically say you could do this I would agree with the inspector since you modified a listed assembly. Your best choice would have been to purchase an equipment ground bar.
 

lrollo

Member
Re: Subpanels

I have installed many GE panels and done it just the way described. I couldnt say for sure the instructions says to do it that way but I believe they do and I have never been turned down for doing it that way.
 

pierre

Senior Member
Re: Subpanels

Brocc
Did you keep the installation instructions? If not have the supply house make a copy and show it to the inspector. Better yet have the supply house call their GE rep and have him fax you a reply saying this installation is acceptable to the manufacturer.
Good Luck

Pierre
 

ryan_618

Senior Member
Re: Subpanels

I see this done all the time and have never failed it. I didn't do residential work, so I've never bought the panels you speak of. Doesn't the bonding jumper you are talking about come with the panel though? I am thinking of the metal jumper that kind of looks like a bent tuning fork. If it comes with the panel and the panel isn't listed as service equipment, what else could it be for? Also, if it is the tuning fork thing, why else would they have that offset that is bent to go directly onto the nuetral?
I think you should fight him on this one.
 