CODE, for one. 250.32(B)(1)Originally posted by jes25:
If the EGC is insulated who cares if neutral current flows on it?
It?s not a silly question, for there is no such thing. What you have to realize, however, is that the EGC is connected to the exterior metal surfaces of every electrical device in the building. That puts every metal object in parallel with each other. Thus, while the insulated EGC is carrying current, and while a person might not care about that, current could also be flowing through the door of the electrical panel as well as the door of the refrigerator, through the lamp stand, through the lighted make-up mirror, and (I suppose it would not be impossible) through the kitchen sink.Originally posted by jes25: If the EGC is insulated who cares if neutral current flows on it?
250.24(A)(5) Load-Side Grounding Connections. A grounding connection shall not be made to any grounded circuit conductor on the load side of the service disconnecting means except as otherwise permitted in this article.
250.142(B) Load-Side Equipment. Except as permitted in 250.30(A)(1) and 250.32(B), a grounded circuit conductor shall not be used for grounding non?current-carrying metal parts of equipment on the load side of the service disconnecting means or on the load side of a separately derived system disconnecting means or the overcurrent devices for a separately derived system not having a main disconnecting means.