I am currently near the end of the design process for a new 115kV/34.5kV substation and my customer want to implement a design that will make the wiring of the substation more efficient and I would like opinions on whether this has been done before and if this is a good idea.
My customer wants to install military grade amphenol connectors on the cabinets of the various substation equipment and at the control building to make the installation of the cables in the field more efficient. They want to do this for all control, CT, PT, and power cables. The breakers, etc would arrive on site with the amphenol connectors prewired and the control building components (relays, AC and DC load centers, etc.) would be wired to amphenol connectors in a box on the outside of the building. They would order the cables with the matching amphenol connetors of the appropriate length so that they could just plug them in on both ends.
My major concerns are:
1) Using this for a CT circuit which could be opened under load. They are looking into seeing if they can find self shorting connectors.
2) Doing this adds additional points of failure (crimping the wire to the amphenol pins and sockets and the male to female connection itself)
3) Moisture ingress causing corrosion issues
Has anyone seen this done before and any other comments would be greatly appreciated. Thank you!
My customer wants to install military grade amphenol connectors on the cabinets of the various substation equipment and at the control building to make the installation of the cables in the field more efficient. They want to do this for all control, CT, PT, and power cables. The breakers, etc would arrive on site with the amphenol connectors prewired and the control building components (relays, AC and DC load centers, etc.) would be wired to amphenol connectors in a box on the outside of the building. They would order the cables with the matching amphenol connetors of the appropriate length so that they could just plug them in on both ends.
My major concerns are:
1) Using this for a CT circuit which could be opened under load. They are looking into seeing if they can find self shorting connectors.
2) Doing this adds additional points of failure (crimping the wire to the amphenol pins and sockets and the male to female connection itself)
3) Moisture ingress causing corrosion issues
Has anyone seen this done before and any other comments would be greatly appreciated. Thank you!