Substation flooring

Status
Not open for further replies.

meroofegypt

Member
Location
cairo
I wanna ask about the substation flooring which contains medium and low voltage switchgear.
Is a must be anti-static flooring such as epoxy or vinyl ) ?
Any recommendations from NEC or IEEE or IEC ?
Thanks in advance
 

Hv&Lv

Senior Member
Location
-
Occupation
Engineer/Technician
Just as a minimum building requirement. Not because of the cables as far as I’m aware.
ours are epoxy painted to seal the concrete.
Vinyl can be a static generator and cause aggravating static shocks
NFPA 101 life safety.
NFPA 77
 

meroofegypt

Member
Location
cairo
nfpa 101 and nfpa 77 don't say directly that the flooring should or as minimum may anti-static. it ensures that flooring should solid (concrete or steel ) to withstand the dynamic and static loads only
i wanna to know which code preferring the anti-static flooring for switch gear room
thanks for your replies
 