Hello,
My question concerns substations feeding main switch gear which in turn powers various parts of our facility.
Outside our plant adjacent to the incoming power & associated transformers we have four (4) large disconnects which then feed four different switchgear in our power house. The switch gear distribute the incoming power to busways and powerpanels throughout the plant. Two of the switchgear are crosstied so that one switchgear could handle the entire load.
Almost two weeks ago, we began to have problems with one of the disconnects outside tripping due to a single phase detector malfunction even though there was no single phase condition present. The current load on this switchgear was on the order of 1800 amps. We operate 24/7, so the decision was made to utilize the crosstie and combine the load of the two switchgear onto the other which had a load of around 2200 amps. Both of these switchgear are nameplate rated at 4000 amps and the ammeter upper limit is 4000 amps. Since we switched, we have noticed a continuous load of 4000 amps which pegs at an approximate value of 4200 amps regularly throughout the day.
The Engineering Director has informed those subordinate to his position that in his experience, we could run these switchgear at 110% capacity and he had done so at other facilities for years.
I personally do not have much experience with this larger switchgear, but due to the smell/discoloration in our powerhouse since the crosstie switch, I thought I would submit this question for your thoughtful response. We have also noticed a voltage drop from 480v to around 455v in the powerhouse with lower voltage readings taken at various points across the plant.
Thanks for your time.
My question concerns substations feeding main switch gear which in turn powers various parts of our facility.
Outside our plant adjacent to the incoming power & associated transformers we have four (4) large disconnects which then feed four different switchgear in our power house. The switch gear distribute the incoming power to busways and powerpanels throughout the plant. Two of the switchgear are crosstied so that one switchgear could handle the entire load.
Almost two weeks ago, we began to have problems with one of the disconnects outside tripping due to a single phase detector malfunction even though there was no single phase condition present. The current load on this switchgear was on the order of 1800 amps. We operate 24/7, so the decision was made to utilize the crosstie and combine the load of the two switchgear onto the other which had a load of around 2200 amps. Both of these switchgear are nameplate rated at 4000 amps and the ammeter upper limit is 4000 amps. Since we switched, we have noticed a continuous load of 4000 amps which pegs at an approximate value of 4200 amps regularly throughout the day.
The Engineering Director has informed those subordinate to his position that in his experience, we could run these switchgear at 110% capacity and he had done so at other facilities for years.
I personally do not have much experience with this larger switchgear, but due to the smell/discoloration in our powerhouse since the crosstie switch, I thought I would submit this question for your thoughtful response. We have also noticed a voltage drop from 480v to around 455v in the powerhouse with lower voltage readings taken at various points across the plant.
Thanks for your time.