I was requested to become the arbitrator for the above subject in between 2 parties.
Background info: the substation is 20.8KV and the HV gear is out in the open enclosed in cabinets.
Party 1 claim that article 110.31 clearance table is the applicable table.
Party 2 claim that article 110.34(E) is tha applicable table.
My approach is as follows:
110.31(D) is the exception for table 110.31 and 110.34(E).
110.31(D) "enclosed equipment accessible to unqualified personnel" exceptions are:
- Ventilating or similar openings in equipment shall be
designed so that foreign objects inserted thru these
openings are deflected from energized parts.
Here is my take on this:
Both 110.31 and 110.34(E) tables refer to " live parts"
if the hv gears are enclosed as described above we have no live parts to worry about and the distance from the fence to the enclosed hv gear is a mute point. I need to focus in the distance from any exposed above the ground live parts such as connection points that are accesible and could cause bodily harm to unqualified personnel and the fence.
However this is not the answer to my question.
The issue is when is table 110.31 applicable versus table 110.34(A) ???
Any feedback will be appreciated.
Background info: the substation is 20.8KV and the HV gear is out in the open enclosed in cabinets.
Party 1 claim that article 110.31 clearance table is the applicable table.
Party 2 claim that article 110.34(E) is tha applicable table.
My approach is as follows:
110.31(D) is the exception for table 110.31 and 110.34(E).
110.31(D) "enclosed equipment accessible to unqualified personnel" exceptions are:
- Ventilating or similar openings in equipment shall be
designed so that foreign objects inserted thru these
openings are deflected from energized parts.
Here is my take on this:
Both 110.31 and 110.34(E) tables refer to " live parts"
if the hv gears are enclosed as described above we have no live parts to worry about and the distance from the fence to the enclosed hv gear is a mute point. I need to focus in the distance from any exposed above the ground live parts such as connection points that are accesible and could cause bodily harm to unqualified personnel and the fence.
However this is not the answer to my question.
The issue is when is table 110.31 applicable versus table 110.34(A) ???
Any feedback will be appreciated.