Flicker Index
- Pac NW
- Lights
The UL standard that covers GFCI's (UL 943) requires that they trip off within 1 second on a 6 mA (milliamp) fault
Is that no longer applicable if the leakage current is non-sinusoidal?
Using a classic Apple 1A/5W charger, I've succeeded fooled a newer style (the kind that won't reset without power on) Leviton GFCI into admitting nearly 100mA rms leakage into ground indefinitely without tripping.
Measured value was 92mA RMS (332mA peak, CCF of 3.6)
This GFCI is great at not nuisance tripping, but it allows certain waveform to leak through nearing 100mA RMS.
To replicate, connect a 5v 1A Apple or similar phone charger like the one shown below across line and ground into a Leviton GFCI outlet. Do it with the adapter unloaded so that its internal capacitor charge up. Sometimes it will charge up and hold. Sometimes the GFCI will trip during the charge up. It may take 2-3 tries.
Once the GFCI holds, apply load to 5v side.
I can load the 5v side pretty close to 1A and Leviton brand GFCI holds indefinitely without tripping. Let's just say not tripping at 0.5A on 5v side.
5V 0.5A is 2.5W, so no matter how you skin it, the input current can not be less than 20.83mArms at 120.0vac at 1.000 PF. That's more than 3 times the UL allowed current.
The implication here is that Leviton GFCI may not respond to a leakage close to 100mA if through a power supply. For example, if you were to touch a lifted neutral of a switch mode power supply load that is connected to a Leviton GFCI.