- New Jersey
- Journeyman Electrician (retired)
I have a 1000 kva transformer feeding a 3000 amp main disconnect that says "Suitable for Use Only as Service Equipment". It's been suggested that if the system bonding jumper is located in the 3000 amp gear then the installation will be compliant. Other suggestions are to remove the link between the EGC bus and the neutral bus and install the bonding jumper within the 1000 kva. Electrically either solution will work but I'm concerned about the listing, others have suggested that it really amounts to nothing more than a sticker on the equipment with some words on it, have the manufacturer change the sticker and either one works. Thoughts?