H Hendrix Senior Member Location New England Jun 16, 2011 #1 What is the answer to an alarm cable for the sump pump in the pit and then run above a dropped ceiling to the panel, as far as not being able to run flexible cord :?
What is the answer to an alarm cable for the sump pump in the pit and then run above a dropped ceiling to the panel, as far as not being able to run flexible cord :?
infinity Moderator Staff member Location New Jersey Occupation Journeyman Electrician Jun 16, 2011 #2 Install the cord in a raceway or move the panel to a place not above the ceiling.