Where is the pump located. If the 120 volt is not cord and plug or not in an area that requires gfci protection then I do not see anything in the NEC that would require GFCI protection.I'm installing a 480V sump pump with a 120V float switch in an industrial facility. Is there any GFI requirement here and if so can you please direct me to the proper article? Thanks.
No GFCI required, the motor must operate by all means or flooding could occur.
For cord and plug connected sump pumps GFCI protection is required. If your sump pump trips the GFCI then you need a new sump
pump.
For cord and plug connected sump pumps GFCI protection is required. If your sump pump trips the GFCI then you need a new sump
pump.
So if the sump pump is in a finished area of a commercial building but not in an area that requires gfci you still need gfci for a cord and plug unit. Where is this written--
Also we are talking the float switch not the pump. The pump is 480V. But I am curious if the pump was 120V same scenario
Dennis, I think we established that in the OPs case there is no need for GFCI, it's hardwired.
John120/240 was responding to the post that implied 'Sump pumps don't get GFCIs because they have to run'
At our last IAEI meeting it was stated that sump pumps do not have to be on GFCI but there has to be a GFCI located within 6 feet of sump pump.
Right, this is in Ohio. Sump pumps are not required to be GFIC. Never like that requirement anyways.