Super rough cost for a MCC?
Todd0x1
CA
Looked at a restaurant building today that had its electrical stripped out while closed. The place had a MCC for all the fans and such, around 16 compartments. Biggest wire to a compartment was #6 most of it was #12-#10. 120/208Y. I know its impossible to price without specs, just wondering ballpark how much is a replacement for this thing? 30K?
I swear I was thinking 30 k before I got to the final part of your post. Also It might depend on how good of terms you're on with the local AHJ.
Will the insurance cover it? We had a customer his insurance had it in the fine print that they will not cover copper theft.
$5 k per section
Section as in per bucket hole and bucket? Or vertical section?
I'd also be curious how a value engineered replacement consisting of a panelboard + gutters + control panels with IEC devices (oversized for increased lifetime) compares cost wise to replacing the mcc.
Vertical section.
I would bet good money I could design a motor control panel that was less money but this is one of those times when having the mcc maybe makes more sense. Hard to tell without taking a close look.
The go/no-go for me with deciding to use a MCC or not is if the motors have VFDs. The drives tend to take up a ton of space in a MCC, and I would rather locate the drive near the motor rather than in a central location. If it was worth adding drives to your motors, I would use a panelboard rather than the MCC.
I haven't designed a MCC for projects outside of a few industrial process lines in many years. The panelboard/switchboard with VFDs is typically less expensive than a MCC, and usually provides more flexibility in the motor control and electrical distribution design.
It is crazy expensive to put the drives near the motors though because of the field labor. We usually build them up in a motor control panel so it is all factory wired up and there is only the field labor of running wires from the panel to the motors. I don't like putting the drives out by the motors because usually they need to be in a box and the box eats up space that most people do not have. plus then you have to run ethernet out there along with power. Just too much field labor.
I was an MCC specialist for a while in the early 80s and had a guestimate value of $2k per section that worked out every time I checked it. Years later when buying MCCs, I found it to still hold true. But that was in the days before VFDs, Soft Starters and smart MCCs were available, it has changed now. I agree with Bob's $5k per section number, but only if it is all hard wired electro-mechanical starters and feeder breakers. Adding a VFD or Soft Start and networking changes that drastically. A couple of years ago I tried to see if I could come up with a new formula, starting off with $5k/section, I couldn't make it work to be useful, too many variables now.
I'm a big proponent of pu8tting smaller (up to 150HP) VFDs in MCCs, especially now with all of the emphasis on safety and arc flash protection. But to each his own.