I have a CT cabinet where my main service disconnect is located. The main bonding jumper is a strap that bonds the neutral to the enclosure, there is no direct connection between the neutral bar & ground bar
My question is - since I only have one available neutral terminal to terminate my water service GEC, can I terminate my supplemental ground rod & building steel bonding conductors to the CT enclosure instead of directly to the service neutral?
NEC 250.53(D)(2), and 250.104(A)(1) seem to support this since this is a service equipment enclosure. I’m just more accustomed to going straight to the service neutral.
My question is - since I only have one available neutral terminal to terminate my water service GEC, can I terminate my supplemental ground rod & building steel bonding conductors to the CT enclosure instead of directly to the service neutral?
NEC 250.53(D)(2), and 250.104(A)(1) seem to support this since this is a service equipment enclosure. I’m just more accustomed to going straight to the service neutral.