klineelectric
Member
- Location
- FL
- Occupation
- electrical contractor
An inspector here is saying I have to add a ground rod to my service which is a 200 amp residential with a concrete encased electrode system (ufer ground) in a monolithic slab. I asked where in the code it says this and he says ( while arrogantly laughing at me) that if it is more than 25 ohms an additional electrode is needed. To which I said did you take an ohm reading....lol. Oh no they wont give us a ground tester, he says. Am I wrong or is the 25 ohms or less only for single rod, pipe or plate electrodes. Thats where im reading it anyway 250.56(2008 nec) or 250.53(2011nec)