opes at askronald
How does NEC 250.53(E) and NEC 250.66(A) apply? Very confusing but the way I interpret this to mean is that with a ground rod at my service, the connection between the service neutral and the ground rod(s) do not need to be larger than a no 6AWG copper when there are no additional grounding connections. Every AHJ I know requires that we size the GEC per table 250.66. Even though I do it some how this does not make sense as the ground rods for the most part maintain equal potential between the building and earth. I question how this larger conductor to earth would create a low impedance ground path without knowing dielectric of the soil. There is a method of checking the dielectric of the soil but would take probably miles between test probes to get an accurate reading. I have been there and done that and there is no practical way to measure the resistance of our earth. How does the larger conductor per NEC table 250.66 help? I can see NEC table 250.66 applying to bonding building steel to the service. Who can clarify this for me? Thanks in advance