NEC 250.96(A) mentions the use of "supplementary equipment grounding conductors." Is there anywhere in the code that identifies the requirements of a supplementary EGC?
Background: There is an existing 400A feeder ran in a 4" EMT with set screw fittings, there is no wire EGC. The engineers at our company do not consider this to be a good practice and we normally provide a wire EGC for each feeder. Is there any way to provide a supplementary wire EGC without having to re-pull the existing feeder? Can a "supplementary" EGC be provided outside the 4"C, or in a different conduit, or would NEC 300.3(B) prevent this?
Background: There is an existing 400A feeder ran in a 4" EMT with set screw fittings, there is no wire EGC. The engineers at our company do not consider this to be a good practice and we normally provide a wire EGC for each feeder. Is there any way to provide a supplementary wire EGC without having to re-pull the existing feeder? Can a "supplementary" EGC be provided outside the 4"C, or in a different conduit, or would NEC 300.3(B) prevent this?