Supplementary Grounding Electrodes

anbm

Senior Member
Location
TX
Occupation
Designer
1. If the building grounding electrode system already has water metal pipe, building steel, UFER, one ground rod - all bond together....
the second ground rod (Supplementary Grounding Electrode) is not required, correct? Because the first ground rod is no longer the sole grounding electrode.

2. How or what tool will be used to meter ground resistance?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
1) The single ground rod is supplemented by the CEE so it's qualifies as an electrode. Since there is a CEE the ground rod is not required.
2) There are a few different types of testers from a hand held to a 3 pole fall of potential tester.

 

anbm

Senior Member
Location
TX
Occupation
Designer
1) The single ground rod is supplemented by the CEE so it's qualifies as an electrode. Since there is a CEE the ground rod is not required.
2) There are a few different types of testers from a hand held to a 3 pole fall of potential tester.

Thanks, what is CEE?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
So without CEE, we need second ground rod?
It gets a bit confusing so I will try and complicate it some more.

If you only have a metallic water line that is in the ground for 10' of more then you need to supplement it. There are many choices but some electricians just drive 2 rods and they are done with it.

If you are able to get a concrete encased electrode installed then you don't need any rods and if there is a metallic water line you would still need that to be a part of the grounding electrode system. So in a sense you have used the water line as an electrode and that must be supplemented and it could be supplemented by a concrete encased electrode or 2 rods, or a few other methods.
 
Last edited:

anbm

Senior Member
Location
TX
Occupation
Designer
It gets a bit confusing so I will try and complicate it some more.

If you only have a metallic water line that is in the ground for 8' of more then you need to supplement it. There are many choices but some electricians just drive 2 rods and they are done with it.

If you are able to get a concrete encased electrode installed then you don't need any rods and if there is a metallic water line you would still need that to be a part of the grounding electrode system. So in a sense you have used the water line as an electrode and that must be supplemented and it could be supplemented by a concrete encased electrode or 2 rods, or a few other methods.
If the building has metallic water pipe, concrete encased electrode, why we need (2) additional ground rods? not one or none?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If the building has metallic water pipe, concrete encased electrode, why we need (2) additional ground rods? not one or none?
You don't. The concrete encased electrode will be the supplement for the water pipe. Think of it this way-- the water pipe is a good electrode however it is often replaced or parts of it replace to where the pipe may no longer be an electrode. This is why the water pipe needs to be supplemented by any of the other electrode choices. Rods are usually the easiest when dealing with existing buildings.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If there is no metal water pipe then we would only need a concrete encased electrode, assuming there are no other electrodes available.
 