OK after a code question came up and was not answered the way i felt it should be i bring it to you for clarification.
By 250.54 supplementary grounding electrodes are not required to to comply with bonding requirements of 250.50(bonding together)or 250.53c(bonding jumper size)or 250.56(ohms)
So lets say i have a supplementary grounding electrode not one that is required in 250.53d2 because of water service but just decided to put in a extra one in,or had a extra rebar poking up what size wire do i have to run to this extra electrode ? Can it be a #12 or does it have to be a #4/0 or is there yet another exception in the NEC that refers me back to 250.53E in which case it has not to be larger than #6 if 250.66 states higher because of conductor size.
Just for clarification the question was stated to me like this :
What size wire do you need to run to a supplementary grounding electrode
my answer was whatever size you have in your truck
correct or not ?
By 250.54 supplementary grounding electrodes are not required to to comply with bonding requirements of 250.50(bonding together)or 250.53c(bonding jumper size)or 250.56(ohms)
So lets say i have a supplementary grounding electrode not one that is required in 250.53d2 because of water service but just decided to put in a extra one in,or had a extra rebar poking up what size wire do i have to run to this extra electrode ? Can it be a #12 or does it have to be a #4/0 or is there yet another exception in the NEC that refers me back to 250.53E in which case it has not to be larger than #6 if 250.66 states higher because of conductor size.
Just for clarification the question was stated to me like this :
What size wire do you need to run to a supplementary grounding electrode
my answer was whatever size you have in your truck
correct or not ?