Re: Suppling power to a detatched garage from the house pane
sbradley71
Is the house panel fed from a disconect switch? If so then yes it would have to be kept seperate. as with the sub panel. But there is an exception to this If you fed the sub panel in the garage with H,H,N. and there is no other metal paths between the house and garage (water,gas,phone,cable) that can become a parallel path for the neutral then you can but the neutral and grounding and the electrode must be bonded together at the sub. But if you have fed this panel with 4-wire then you must keep the neutral and grounding seperate. and and removeing that jumper is one way to do it as long as the manufacture allows it. and if your going to have more than 6 circuits It will need a main breaker for means of disconnect.