I have a step up transformer 208v to 480v (45kva) which feeds a fused switch that has 30 amp type J fuses. This switch then feeds a VFD panel which supplies a 480v 15 hp supply fan and a 480v 15 hp return fan. After reviewing this, aren't the 30 amp fuses too small?
A 15 hp 480v motor has a full load of 21 amps. If there are (2) motors on the same circuit don't I take the first motor X 125% ( I think i can go up to 175%) + the full load of the next motor 21 amps and come up with 47.25?
So I would have 50 amp fuses in a 60 amp disco?
Thanks in advance for the feedback