Supply bonding jumper at transformer or at first point of disconnect main panel?

Status
Not open for further replies.

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
To my understanding the neutral is to be bonded to grounds only at one location to mitigate objectionable currents. For this reason you cannot ground the neutral within both the transformer and at the main bonding jumper in main panel/ first point of disconnect.


Therefore, if you are installing or inspecting a main panel and there is no main bonding jumper bonding ground, neutral and metal of main panel then how would you know it has been done at the transformer?

If you assume it was not done at transformer and place one in the main panel / first point of disconnect but the transformer had one then you’ll have code violating objectionable current.
 

SSDriver

Senior Member
Location
California
Occupation
Electrician
One or the other. You would have access to the transformer and the panel. POCO transformers don't matter, you bond at main panel(or meter) if a service. POCO will have requirements of where they want YOU to bond at.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If the transformer is a utility transformer as SS mentioned then it doesn't matter. If the transformer is an SDS then the either location rule for the SBJ would apply.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
........then how would you know it has been done at the transformer?......

If the SBJ is not in place you likely won't show any continuity between neutral and grounding conductors and/or if the system is active, you will show erratic voltages to ground.
Just a couple of points of order, there are exceptions that allow a SBJ at both the source and 1st disconnect and your GEC should be connected at the same point as your SBJ.
 

Jpflex

Electrician big leagues
Location
Victorville
Occupation
Electrician commercial and residential
The transformers are utility owned and pole mounted so I don’t have access to them. However, there was no bonding jumper in main panel first point of disconnect between neutral/ground buss and metal panel case. This is what got me wondering
 

xformer

Senior Member
Location
Dallas, Tx
Occupation
Master Electrician
The transformers are utility owned and pole mounted so I don’t have access to them. However, there was no bonding jumper in main panel first point of disconnect between neutral/ground buss and metal panel case. This is what got me wondering
........then how would you know it has been done at the transformer?......

If the SBJ is not in place you likely won't show any continuity between neutral and grounding conductors and/or if the system is active, you will show erratic voltages to ground.
Just a couple of points of order, there are exceptions that allow a SBJ at both the source and 1st disconnect and your GEC should be connected at the same point as your SBJ.
Most residential service drops are either aerial, which cannot have objectional current on the aerial drop or pvc from underground which can't carry current due to its high impedance composition. So, for residential, bonding neutral to ground at the utility Transformer, and bonding again at the first means of disconnect is permissible. The bonding of the Neutral at the first means of disconnect is required by the NEC. The Poco has their own codes to follow.
 

augie47

Moderator
Staff member
Location
Tennessee
Occupation
State Electrical Inspector (Retired)
If they are POCO transformers then you dealing with services and not SDS and as xformer states 250.24/250.28 require a main bonding jumper at all service disconnects on grounded systems (250.20) . There is rarely a path for "objectionable current" and, in the rare event there is one, it is acceptable.
 