Jpflex
Electrician big leagues
- Location
- Victorville
- Occupation
- Electrician commercial and residential
To my understanding the neutral is to be bonded to grounds only at one location to mitigate objectionable currents. For this reason you cannot ground the neutral within both the transformer and at the main bonding jumper in main panel/ first point of disconnect.
Therefore, if you are installing or inspecting a main panel and there is no main bonding jumper bonding ground, neutral and metal of main panel then how would you know it has been done at the transformer?
If you assume it was not done at transformer and place one in the main panel / first point of disconnect but the transformer had one then you’ll have code violating objectionable current.
Therefore, if you are installing or inspecting a main panel and there is no main bonding jumper bonding ground, neutral and metal of main panel then how would you know it has been done at the transformer?
If you assume it was not done at transformer and place one in the main panel / first point of disconnect but the transformer had one then you’ll have code violating objectionable current.