I have a supply fan that is totally outdoors but is in a area of sewer gas . The supply fan is in a large vent pipe candy cane, that supplies air into a wet well which is a metering pit for waste water. The motor is a explosion proof 3/4 h p .The feed originates from a meter cabinet which is about 25 foot away. The engineer states that the supply pipe which has the motor totally mounted inside is class 1 div 2. A barrier of 3 foot around outside of the pipe is class 1 div 2. ART 501 states I need a barrier within 10 foot. Do I need a EY fitting as stated within 10 foot, if the exception 501.15 exception 4 notes if all 5 conditions are met . He wants a E Y where the feed enters into the meter cabinet panel. I will install a E Y in the non classified area and wanted to install one at the motor (even though) the motor is sealed at the pecker head is this a over kill what do you guys think .The feed is in 3/4 conduit all the way. I have some coming up that are half underground thanks :?